    Customer has a glycol system, with pump not running glycol will come down to 29 deg with no problem.
    With pump on unit runs upper 40's.
    Refrigeration pressures are fine, can old/bad glycol cause this??

  • #2
    could be old glycol, especially if it the rv type and not the type meant for circulation. If it is older than 18 mos, swap it out. Also check the run of the trunkline, insulation wrapped properly, not run on heat ducts or pipes, etc.
    Happy Tappy Draft Beer Services
    Serving Mid-Michigan and beyond

    Comment


    • #3
      Is the trunk line run in a floor chase? If so, bet the chase is flooded. Flooded chases are major problem here in Virginia.

      Comment


      • #4
        Same here DC , it sounds like you have a flooded chase.

        Comment


        • #5
          Flooded chase from what the chase should be pressure check,so no ground water, at less 2-4 inches above floor/ If the chase is flooded yoiu have a leak!
          L. Tapper

          Comment


          • #6
            Larry

            Chases here flood with ground water from poorly installed chases. Most of DC and Virginia is a flood zone/swampy type of area. I've pumped chases dry and have seen them flood within minutes.

            Old trunklines from the P company were not waterproofed so flooded chases saturate and foul the trunklines very quickly.

            Dennis

            Comment


            • #7
              Originally posted by Larry Tapper View Post
              Flooded chase from what the chase should be pressure check,so no ground water, at less 2-4 inches above floor/ If the chase is flooded yoiu have a leak!

              If so, bet the chase is flooded. Flooded chases are major problem here in Virginia.