I have a Perlick 4410 line chiller on a 120' run. It has been fine for almost 2 years. Within the last two weeks, it has begun to freeze some of the lighter alcohol beers, and now freezes everything under 5%abv. The glycol level is normal and the mixture is 80/20 glycol/water.
The front panel readout says 61F, for the reservoir. However, I get 27F from a reading with a calibrated thermometer. I am suspecting a flaw in the thermal probe, but the manual says the chiller should cycle every 5 minutes if the probe goes bad. That is not happening. It is running constantly.
Is the probe replacable? I don't even see it, easily. Second, is there a software calibration for the temp probe?
The front panel readout says 61F, for the reservoir. However, I get 27F from a reading with a calibrated thermometer. I am suspecting a flaw in the thermal probe, but the manual says the chiller should cycle every 5 minutes if the probe goes bad. That is not happening. It is running constantly.
Is the probe replacable? I don't even see it, easily. Second, is there a software calibration for the temp probe?