I had a similar problem as just mentioned above. My set up was as follows:
- Full Size Kenmore side-by-side refrigerator
- 12' 1/4" ID beer hose
- 15 CFM Blower and hose
- 10 PSI
I set this system up per this link found on this site -->
http://www.micromatic.com/beer-quest...r-aid-106.html
The document recommended a 1/4" ID beer hose due to the length of my run (10 feet from top of keg to beer faucet).
My first two kegs through this setup generated 1/2 foam on the first pour and a perfect pour right after that. Pouring another beer after about 15 minutes would be exactly the same. The beer was flowing pretty fast our of the faucet on each pour so I believed my problem to be presure related. Several adjustments to the CO2 resulted in no improvement.
I was finally able to correct my problems by doing the following:
- replaced the 12' 1/4" ID beer hose with 12' 3/16 ID beer hose
- placed the beer hose inside of the blower hose to keep the beer line cold up to the tower.
As most standard kegerators come with a 3/16" ID hose (typically five feet), I would perhaps recommend obaining a longer run of hose. This, in theory, should increase the restriction of the beer flow, which in turn should slow down the pour rate without having to sacrifice the PSI of the CO2.
Just my thoughts....
Dave