    Default Ice on BM23 lines

    Hi all,
    Sorry I don't know the correct terminology for the parts in question. I bought a used Beverage Air BM23. I have a pitcher of water down to about 39 degrees by setting the thermostat to 20 degrees F. I have ice that is building on the back of the lines as pictured. The unit seems to run constantly (I haven't seen it kick off) and the ice thickens over time. Is there a problem here?
    I included a pic of the inside as well. I'm not sure if it matters. I doubt the ice is normal, but I wanted to find out. thanks for the help.


  2. #2
    THE ICEMAN's Avatar
    THE ICEMAN is offline Super Moderator
    Join Date
    Dec 2007
    Location
    Sun Devil Country
    Posts
    609

    Default

    It looks like someone has been into the sealed system at some point in the units life. There has been a service valve added to the system, those units do not come with them.

    That having been said, your unit is a "critical charge" type of system meaning it takes a very specific amount of refrigerant for it to work properly. Too much or too little refrigerant will hurt the performance. Given that those units only take less than a pound of refrigerant, typically from 6 to 10 ozs, it doesn't take much to upset the balance. Also given the ice on the suction line, your system looks to be slightly overcharged.

    It's easy enough to fix if you know what you are doing. I'd like to tell you how but it can be screwed up as easily as it can be fixed. Plus you need to be certified to work with freon. You will need to contact a service company that is familiar with those systems, not just an A/C company.


    THE ICEMAN
    Last edited by THE ICEMAN; 11-08-2009 at 03:26 PM.
    My conversion >>>---->>> KILLER KEGERATOR


    "Without question, the greatest invention in the history of mankind is beer. Oh, I grant you that the wheel was also a fine invention, but the wheel does not go nearly as well with pizza."
    -Dave Barry-


  3. #3
    clivus is offline Junior Member
    Join Date
    Oct 2009
    Posts
    3

    Default

    Thanks for the reply. It is cooling a pitcher of water to 34 degrees consistently. The ice has gotten worse. I'm going to have someone come look at it. I'm on the fence deciding whether the unit is worth me salvaging.

  4. #4
    THE ICEMAN's Avatar
    THE ICEMAN is offline Super Moderator
    Join Date
    Dec 2007
    Location
    Sun Devil Country
    Posts
    609

    Default

    A couple questions for you... Is that the only place the ice forms & is line kinked at all or is there a weld joint there?

    When a unit is overcharged, the ice will form all along the suction line all the way back to the compressor. If that is the only place the ice forms then there could be a restriction in the line.


    THE ICEMAN
    My conversion >>>---->>> KILLER KEGERATOR


    "Without question, the greatest invention in the history of mankind is beer. Oh, I grant you that the wheel was also a fine invention, but the wheel does not go nearly as well with pizza."
    -Dave Barry-


  5. #5
    clivus is offline Junior Member
    Join Date
    Oct 2009
    Posts
    3

    Default

    Thanks for the help. The suction line will occasionally frost back to the compressor, but the ice only gets as big as in the second picture.
    Miraculously, I came out this morning and the ice was gone. The line will frost over and then melt while I watch it, but no more ice. It may have been a non-condensable.
    I put a 1/4 barrel in there tonight. Now I'll try to get the temp right.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Note:
Micro Matic’s Draft Beer Discussion forum is a public service which allows our members to share their draft beer knowledge and for visitors to view their discussions. While Micro Matic's Dispense Institute instructors and knowledgeable staff are often participates in the forum, Micro Matic does not attempt to verify information posted by members. The information which members post are personal views, and may not reflect the views of Micro Matic. Micro Matic takes no responsibility and assumes no liability for any information posted by members, or results that occur from the information. Micro Matic reserves the right to monitor, remove or edit content at its discretion.