Old 06-21-2008, 09:30 PM
xcasey69 xcasey69 is offline
Junior Member
 
Join Date: Jun 2008
Posts: 3
Unhappy Beverage Air BM23 not cooling properly

I have a Beverage Air BM23 that is not cooling properly. When I first plug it in, it cools properly and then within a day gets up to 55-60 degrees. Could this be just caused by being low on freon? Can anyone tell me how to charge it? I did see that it uses R134 and not R12. I am trying to find a serive company in the Denver area, but thought I might try to charge it myself if possible. I was told be a refrigerator repairman that it is a sealed unit and will likely require compenent replacement. Any information that can be provided would be greatly appreciated. I want to get back to drinking cold beer from it again soon!
Reply With Quote
  #2 (permalink)  
Old 06-22-2008, 04:52 AM
THE ICEMAN THE ICEMAN is offline
Super Moderator
 
Join Date: Dec 2007
Location: Sun Devil Country
Posts: 276
Default

In order to recharge the system you must be certified to work with refrigerants. And if it needs recharging, it means you have a leak in the system which would require a leak detector.

From what you describe it sounds like the evaporator coil might be freezing over. Is the evaporator fan running? Does the compressor run continuously? Is the temperature control set too cold?

THE ICEMAN
__________________
The liver is evil, it must be punished!


"Without question, the greatest invention in the history of mankind is beer. Oh, I grant you that the wheel was also a fine invention, but the wheel does not go nearly as well with pizza."
-Dave Barry-
Reply With Quote
  #3 (permalink)  
Old 06-22-2008, 12:20 PM
xcasey69 xcasey69 is offline
Junior Member
 
Join Date: Jun 2008
Posts: 3
Default

How do I check these things? I am new to this as this is the first time I have had any problems with the kegerator.
Reply With Quote
  #4 (permalink)  
Old 06-22-2008, 12:36 PM
THE ICEMAN THE ICEMAN is offline
Super Moderator
 
Join Date: Dec 2007
Location: Sun Devil Country
Posts: 276
Default

Quote:
Originally Posted by xcasey69 View Post
How do I check these things? I am new to this as this is the first time I have had any problems with the kegerator.
The evaporator is located inside towards the top of the kegerator. Take a flash light & look up through the grill where the fan is & see if you see any ice on the coil & if the fan blade is turning. The fan should run all the time. You can also reach up behind the coil & feel for an ice buildup. The temp control is typically numbered 1 to 9 with 1 being the warmest. A 4 setting is a good starting point. The compressor should not run continuously. With the door closed it should cycle on & off anywhere from 5 to 15 min.

THE ICEMAN
__________________
The liver is evil, it must be punished!


"Without question, the greatest invention in the history of mankind is beer. Oh, I grant you that the wheel was also a fine invention, but the wheel does not go nearly as well with pizza."
-Dave Barry-
Reply With Quote
  #5 (permalink)  
Old 06-22-2008, 01:10 PM
xcasey69 xcasey69 is offline
Junior Member
 
Join Date: Jun 2008
Posts: 3
Default

I have had it unplugged for a while. I plugged it in and the fan is running all the time. The thermostat was at 9 and I turned it down to 4. I noticed the door seems to be sagging and there is a gap around the top where the seal is. IS there an adjustment to the door somewhere? I also notcied the copressor seems to be clicking on for only a few second and back off regularly. Is this a sign of low freon and that I should unplug it or am I alright to let it run a while and see what happens.

Thanks for the help!
Reply With Quote
  #6 (permalink)  
Old 06-22-2008, 01:53 PM
THE ICEMAN THE ICEMAN is offline
Super Moderator
 
Join Date: Dec 2007
Location: Sun Devil Country
Posts: 276
Default

Quote:
Originally Posted by xcasey69 View Post
I have had it unplugged for a while. I plugged it in and the fan is running all the time. The thermostat was at 9 and I turned it down to 4. I noticed the door seems to be sagging and there is a gap around the top where the seal is. IS there an adjustment to the door somewhere?
IIRC there is not much of an adjustment on the doors. Check the pivots & see if they are worn.
Quote:
Originally Posted by xcasey69
I also notcied the copressor seems to be clicking on for only a few second and back off regularly. Is this a sign of low freon and that I should unplug it or am I alright to let it run a while and see what happens.

Thanks for the help!
It sounds like you have a problem with the compressor. There is no pressure control on a unit of that size so a low freon condition is not a factor. The compressor may have overheated due to a bad condenser fan (near the compressor) or a dirty condenser. Check those, unplug the unit & let the compressor cool for a few hours. If you're lucky, after a few hours, the compressor will start up & run. If not the compressor "might" be locked up. You will need to get a service company to confirm this. To give you an idea, if my company were to replace the compressor it would be in the $600 to $800 range.

EDIT: If the unit is 5yrs or less, the compressor should be covered under Bev Air warranty.

THE ICEMAN
__________________
The liver is evil, it must be punished!


"Without question, the greatest invention in the history of mankind is beer. Oh, I grant you that the wheel was also a fine invention, but the wheel does not go nearly as well with pizza."
-Dave Barry-

Last edited by THE ICEMAN; 06-22-2008 at 03:42 PM.
Reply With Quote
  #7 (permalink)  
Old 06-22-2008, 07:07 PM
Scott Zuhse Scott Zuhse is offline
Super Moderator
 
Join Date: Mar 2005
Posts: 1,584
Default

Is the condenser clean?
__________________
Scott Zuhse, Instructor Micro Matic Dispense Institute
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -7. The time now is 05:30 AM.

Note:
Micro Matic’s Draft Beer Discussion forum is a public service which allows our members to share their draft beer knowledge and for visitors to view their discussions. While Micro Matic's Dispense Institute instructors and knowledgeable staff are often participates in the forum, Micro Matic does not attempt to verify information posted by members. The information which members post are personal views, and may not reflect the views of Micro Matic. Micro Matic takes no responsibility and assumes no liability for any information posted by members, or results that occur from the information. Micro Matic reserves the right to monitor, remove or edit content at its discretion.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.0.0 RC6 © 2006, Crawlability, Inc.