Testing Glycol System
I am a newbie with enough knowledge to be dangerous. I am working with an older glycol system that doesn't want to cool below 46 degrees F. That is temp temp of the beer at the faucet. It is circulating glycol and is adjusted to the coldest setting. The glycol level is okay and the walkin/product temperature is 34-36 degrees. My questions are as follows.
1. What temp should the glycol resevoir (bath) be if ambient is 60 F.?
2. How can you test efficiency of the glycol itself (hydrometer, lab) ?
To make matters worse, the new owners of this system know nothing about it and with out a dissasembly, I can not tell if the towers (2 X 4 product) are true glycol units or how long the run is. I am assuming 40-50 foot.
Thanks for the help
Beer is good
|

04-23-2006, 09:31 AM
|
|
Senior Member
|
|
Join Date: Jan 2006
Location: Plains,PA , USA.
Posts: 169
|
|
What is your glycol temp? You seem to have taken the temp. in the cooler, at the faucet, and the ambient air but noticably left out the glycol temp.
|

04-24-2006, 07:04 AM
|
|
Senior Member
|
|
Join Date: Apr 2006
Location: Mid Michigan , USA.
Posts: 79
|
|
I did not take a reading, at least did not write it down, of the glycol bath. It was much colder than the ambient but seemed warmer than the cooler. Should the glycol be at dispense temp ? or should it be slightly warmer due to heat exchange.
Thanks for the previous reply.
Beer is good
|

04-24-2006, 07:09 AM
|
|
Senior Member
|
|
Join Date: Apr 2006
Location: Mid Michigan , USA.
Posts: 79
|
|
I might have found my own answer, glycol is supposed to be 32 F+/- 2 F. Is that correct.
Beer is good
|

04-24-2006, 12:20 PM
|
|
Senior Member
|
|
Join Date: Feb 2006
Location: , , USA.
Posts: 115
|
|
Anheuser - Bush says 29 degrees. Most new chain restaurants set them at 30F.
|

04-25-2006, 08:09 AM
|
|
Super Moderator
|
|
Join Date: Mar 2005
Posts: 1,481
|
|
The glycol chiller should turn off at 29 degrees and turn back on about 32. Be certain that the condenser is clean with no dust accumulation. Also, be certain that the thermostat bulb is submersed in the bath and not against the coils. Hopefully the bath is not freezing against these coils.
Use a refractometer to test the glycol freeze point. You should have around a zero to five plus degree bath freeze point on most units less thin plate heat exchangers (no coils).
Scott Zuhse, Instructor Micro Matic Dispense Institute
|

04-25-2006, 04:40 PM
|
|
Senior Member
|
|
Join Date: Apr 2006
Location: Mid Michigan , USA.
Posts: 79
|
|
Scott and All,
Thank for the input. Glycol bath is not even near that cold. I checked the condensor coils (automotive background) and made sure it is breathing properly. I have a refractometer from wine making and pop brix-ing days and will check. Thank again.
Jim
Beer is good
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
All times are GMT -7. The time now is 11:42 PM.
Note:
Micro Matic’s Draft Beer Discussion forum is a public service which allows our members to share their draft beer knowledge and for visitors to view their discussions.
While Micro Matic's Dispense Institute instructors and knowledgeable staff are often participates in the forum, Micro Matic does not attempt to verify information posted by members. The information which members post are personal views, and may not reflect the views of Micro Matic. Micro Matic takes no responsibility and assumes no liability for any information posted by members, or results that occur from the information.
Micro Matic reserves the right to monitor, remove or edit content at its discretion.
|
|
|