Default Problem beer lines

I have encountered a problem at a customers bar and was looking for some support and/or second opinions on my diagnosis before heading out there…

The system is a glycol chilled long draw system servicing 2 towers (one is 50 feet and the other is 25-30 feet away) using 75/25 at 20lbs to push the beer. The cooler is one floor below the bar(s). The first run is the main bar, the second is to a service bar that will not be used for another month or two.

The problem is that some of the lines are pouring intermittently, slowing to a trickle and turning to foam. Sometimes not pouring at all or pouring foam.

My diagnosis is that something must be blocking the line because the service bar still pours when the ones at the main bar do not. I did not really inspect the second run but will do that when I am in next. The glycol unit is set at 30 with a 7-8 degree differential and the freeze point of the mix is 31 degrees. This seems to support my theory. I recommended servicing the unit which will include flushing the glycol out and replacing it with fresh glycol mix, cleaning out the dust from the cooling unit and resetng the thermostat for 29 and the differential down to 3 degrees. I am assuming that the service bar run is not as insulated or runs through a warmer part of the building which is why it is not freezing and the main bar is. Is there anything else I should be looking at? Does my diagnosis seem accurate? I want to get this up and running for them as soon as I can so I want to be prepared. Thanks in advance for any help.
__________________
Ed
Blue Line Draft Systems
www.bluelinedraft.com
Reply With Quote
  #2 (permalink)  
Old 06-05-2007, 09:03 PM
Larry Tapper Larry Tapper is offline
Senior Member
 
Join Date: Mar 2006
Location: , , USA.
Posts: 118
Default

Take a temp reading of the out glycol line and the return line, the system my not be large enought ot take care of both runs. they longest run should be the first lines cooled. How old is the system? Lots of things to Know just to help out, good luck.
__________________
L. Tapper
Reply With Quote
  #3 (permalink)  
Old 06-06-2007, 05:43 AM
edramshaw edramshaw is offline
Moderator
 
Join Date: Feb 2006
Location: , , .
Posts: 500
Default

Thanks. The system is on the older side. I will take take the temp of the send/return lines when I head up there. I could see why that would cause beer to foam but not to freeze, any thoughts?
__________________
Ed
Blue Line Draft Systems
www.bluelinedraft.com
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -7. The time now is 08:21 AM.

Note:
Micro Matic’s Draft Beer Discussion forum is a public service which allows our members to share their draft beer knowledge and for visitors to view their discussions. While Micro Matic's Dispense Institute instructors and knowledgeable staff are often participates in the forum, Micro Matic does not attempt to verify information posted by members. The information which members post are personal views, and may not reflect the views of Micro Matic. Micro Matic takes no responsibility and assumes no liability for any information posted by members, or results that occur from the information. Micro Matic reserves the right to monitor, remove or edit content at its discretion.


Powered by vBulletin® Version 3.7.1
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.0.0 RC6 © 2006, Crawlability, Inc.