    I am planning to install a multiple tap system in my bar and do not have room at the bar for a larger kegorator. I was planning to route the beerline through a closet and into my garage where I would set up a full size fridge (with a top freezer) for my kegs. My run will be close to 20' with several tight bends. Most people on this site say air cooling does not work well at those longer lengths and with several bends. I think I need glycol cooling.

    I thought I could purchase a full size fridge with a freezer on top. I would place a tub with a fountain pump in the freezer and use that to cool my beer lines. I could use the freezer thermostat to keep my coolant at 29F, then use the refrigerator thermostat to keep my beer at 38F.

    1. will this be an effective way to cool? what issues may I have? How large of a container of coolant should I have?
    2. are the standard fridge controls good enough to regulate the beer temp or do I need to purchase a Jonson type controller?
    3. I noticed glycol towers tend to be a bit more pricey. What are the issues with simply routing my cooling lines up into an air cooled tower?

  2. #2
    Jay1 is offline Senior Member
    Join Date
    May 2008
    Location
    Calgary Alberta
    Posts
    152

    Default

    Hi,

    I have 30'ft and I setup a pretty good air-cooled system. I didn't have your bends. I have read (perhaps here someplace) that each 45 bend is like adding 5ft.

    I have since upgraded to Glycol......

    I used a 4" PVC for my return air, inside that I ran a 2" which ran the cool air into the tower and within that my beer line. The 4" was sealed to the bottom of the bar while the 2" went 1/2 way up the tower. This way as the cold air fell it was drawn back through the 4".

    All was going fairly well - My foam was well managed but the first draw from the tower was not so cold so I ended up dumping the first 3/4 of a pint if I had not been using the tower in the past 24hrs.

    The turn for the worse came this summer. I don't have A/C (I am in Canada and its not needed) and we were in a bit of a heat wave. This is when I noticed my tower had a fair bit of condensation on it. I went to check the temp of the freezer and the side of the beast was hot (very hot to the touch). Escentially what was happening is that my tower was acting as a heat exchanger and the freezer couldn't keep up.

    The Glycol system:
    I have a fountain pump and a 5gal bucket that is pumping glycol to the tower and then circulating back to the bucket.
    - Here are my learnings:
    Water has better heat transfer properties than Glycol so only add enough glycol that your fluid doesn't freeze. I initally filled my bucket with straight no-mix glycol. You can get this (cheap) at any RV place as they use it for winterizing motorhomes. I have since drained more than 80% and replaced it with water.
    - You need a big enough reseivor so that by the time you pump the fluid back to the tower the warm stuff has had a chance to cool down again.

    I am using a chest freezer for everything. Works well. I have since learned that a Glycol Engine (used in professional settings) is a small freezer that keeps the glycol signficantly cooler than what the beer is stored at. This allows the line to remain at the same temp as what the beer is stored at. In your case using the fridge for the beer and the freezer for the glycol is a brilliant idea.

    I hope I don't get crucified for the next statement but I "think" a tower that is designed for glycol actually has couplings on the bottom for glycol lines and these run close to the stainless beer shanks in the tower.

    My tower had no such fittings so I simply wiretied the glycol lines up the beer shanks and used a metal u fitting on the two glycol lines right over the spot where the shank goes into the tap. I then wrapped everything in tinfoil to increase the conduction between the lines.

    Finally with my freezer which was supposed to have a range from +5 to -25 (this is celcuis) 0 = 32 was not accurate at all. I ended up getting one of the miromatic controlers (brewers choice) and it now controls my freezer.

    Good luck with your project, good questions, you won't be sorry.

  3. #3
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    Thanks for the advice. You have answered many of my questions and have provided some good tips I intend to follow.

    It sounds like glycol is a requirement to do this or at least a more robust method.
    It also sounds like I should plan to have several galloons in my freezer, I suppose I might be able to get a way with less the cooler it is (as long as I do not freeze my lines and keep my %glycol at min)

    I will plan to buy and wire in a replacement controller for the beer compartment. I have read that temp variations screw with the pressure and flow.

    It also sounds like I might be able to get creative with my cooling lines and save a couple $$ with an air cooled tower. Some come both ways and I was wondering if they put something special in there. It sounds like if they do, it may not be necessary, if I DIY some added insulation and tie the cooling line to the individual beer lines in the tower.

    You are correct the glycol towers I have seen simply have connections at the bottom. I suspect it is simply for commercial applications to save time and having to customize the tower. Some towers I noticed only come in glycol, they look like they simply do not have much space for air flow.

    Thanks for the advice.

    Anyone have a similar system?

    JJtom

  4. #4
    cubby_swans's Avatar
    cubby_swans is offline Super Moderator
    Join Date
    Nov 2007
    Location
    St. Louis, MO
    Posts
    2,791

    Default

    make sure you find something that will allow the freezer to get that warm. Most freezers will not allow you to set them that warm (29F). Mine at home has a digital controller built in and has an upper threshold of 8F.
    ____________________________________________
    Our beer, which commeth in barrels, hallowed be thy drink
    Thy will be drunk, I will be drunk, at home as it is in the tavern
    ____________________________________________


    Home Brew IPA

  5. #5
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    More good experience. Thanks.

    Looks like I will have to remove both the thermostat for the fridge and the freezer and replace them both with a Johnson, ranco or brewers edge type of controller. There goes the warrantee on the fridge!

    Any recommendations on controllers? Control, ease of wiring for this application ect.?

    tom

  6. #6
    Jay1 is offline Senior Member
    Join Date
    May 2008
    Location
    Calgary Alberta
    Posts
    152

    Default

    If you get the Micromatic one you don't need to do modify anything.

    You simply put the fridge/freezer or whatever your using for a cooler on its max settting. The Micromatic plugs into the wall - and then the cooler plugs into the controller. The controller simply cuts the power. A temp prope sits inside of your cooler and monitors the temp.

    Dead easy and no warranty violations.

    Of course I cut mine directy into the compressor so thats another story.

  7. #7
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I have completed my conversion and am ready to buy my first keg for this system. I have read many posts and tried to piece together as many best practices as I could. It is a remote 3-tap “t” tower that I converted to glycol, I made my own trunk lines, converted the top freezer to pump and control my coolant at 29F and the bottom fridge for up to 3 kegs at 36F.

    The reason I did not go with air cooling is that although I have a closet behind my bar, it is actually the space under a staircase. I did not want a chest freezer, since there would be too much lifting in a confined area and I likely would break things restocking after a few beers. I wanted a vertical fridge that is easy to get at, easy to load, with plenty of room to more easily maintain.

    What I did will void your warrantee. (This is not the exact order, the order is purely to help convey the method):

    I will spare you my testing, planning and investigation details and fast forward to the conversion. My budget was $1400, which was the cost of a good two tap self contained unit that can hold 4 corny kegs with all the supplies (tanks, taps, etc.) I ended up around $1200, but still would like to buy some odds and ends. Big ticket items – $415 for fridge (Menards), $321 for air cooled tower with 3 Perlick 525 SS’s, two Ranco ETC’s at $55 each.

  8. #8
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I am working now to figure out how to post pictures.

  9. #9
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    Freezer conversion:
    Most low end refrigerators have a single temp controller, to my disappointment. The way they (mine) was designed to work was to control the fridge by cooling the freezer and using a knob adjusted damper to diver air to the lower box until it is at the desired temp an let the freezer be less controlled. I decided to reverse that with the two Ranco’s. They are digital and seem to be much nicer and more precise than the Johnson. They measure temp directly and have set back amounts, very nice for the same price as a Johnson. I bought them from a heating and AC place online, not a beer store. Much cheaper.



    Then I noticed where and how the cool air enters from the freezer (from the damper control) and glued some lexan over the fridge cooling vent (more on why later). I also noticed during my testing that this fridge has a timer that automatically defrosts after 10 hours of run time, it shuts off for 30 mins to defrost the coils. There is a drain next to the fridge cooling vent, I needed to be careful not to cover that thing up or the cooling unit in the freezer would not drain while it was defrosting.

    You can see here the drain pan and the fitting that goes to the tube in the back of the fridge, this is how my fridge drains - down to the floor for to a drainage pan by the compressor.

    let's see if the photo's attatch for me.
    Attached Images Attached Images

  10. #10
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    Then I ran external power up the freezer control (mounted to the outside of the fridge). Using a wiring diagram for my fridge I got at the manufactures’ website, I located the temp control wires. They were located in the assembly at the top of the lower box. I noted that the fridge is cycled on/off simply by making contact of the two wires. Utilizing both the wiring diagram of the fridge and the Ranco, I now had the Fridge temp control replaced by the Ranco to control my freezer only. I then ran the probe to the freezer and fastened things to the outside.

    I added a junction box to the side to make all terminations to incoming power chord to both temp. controls, water pump and new fans (stay tuned). I also mounted two switches there one for the water pump and one for the rest of my add-ons. So I can run the fridge with or with out the water pump. A nice to have that also helped during testing.
    Attached Images Attached Images

  11. #11
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    Now the fridge:

    The controller on the left is for the fridge. My plan was to simply use that to drive computer fans through two holes in the floor of the freezer, one fan blowing out and one blowing in. A word of caution, when drilling into your fridge, be careful to unplug it. I ended up cutting through some wires and had to repair them with some moisture proof epoxy.

    But with my fridge diagram, some silicone, and some Great Stuff foam, I was back on my way.

    I attached the two fans to some ABS fittings, I sized them to the ID of the ABS – 2” – 60x60x30 mm fans @ 10.2 CFM each. I used a 2” hole saw, so I had a good fit and used some silicone. I wired them to the fridge controller. When the temp drops, the fans kick in and draw cool are from the much colder freezer.

    I then made some blocks to put my glycol tank on (a plastic tub) to keep it over my fans and make sure I got as much heat transfer to the bottom of the reservoir as possible.

    I wired my cooling pump, to be located in the pan. I used 20’ of copper 3/8” od copper coil on my return line to help with heat transfer on the way back (it did not work with just the pan, I added 10 feet of copper, it still did not cool as fast as I wanted. I wanted it to be close to the freezer temp by the time it returned). The freezer fan blows directly on the coil return line. I also did not want the coil in the reservoir, since that may warm the return line slightly. I drilled holes in the top of the freezer and dropped bolts through to hang the copper coil.
    Attached Images Attached Images

  12. #12
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I then made trunk lines with three ¼ inch ID beer lines, vinyl, ½ o.d. I wrapped them with aluminum tape, then with vinyl tape (I found that the window flashing tape at my home improvement store worked very well at a good price and was 4” wide). I then wrapped them with water line foam insulation and wrapped the bundle with black Duck tape. My trunk line was large, so to get the larger ID, I used more than one piece. I used 3/4” thick foam. I actually ran my lines first then began the taping and insulation process to make sure my lengths were good. My tower came with several feet of 3/16 beer line, I left that in place as that seemed to be the recommendation from what I read.

    I ran them through my closet and out to the garage, about 20' of beer line.

    I modified my tower with copper cooling lines – 3/8 ID and used cable ties to hold the beer lines in contact. I also ordered cooling blocks that attached to my facet shanks, and ran the copper through that with some sweat fittings. Then I put some gasketing on the top of my tower to prevent air flow and condensation.

    Sealed off the beer lines, coolant lines, electrical connections and start thing up. Using water my coolant is maintained at 24 F and the water pours out of my faucet at 32-33F (recently bumped it up to 34 to keep the water from freezing.)

    I just installed my first keg beer at 36F
    Attached Images Attached Images

  13. #13
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    more pictures
    Attached Images Attached Images

  14. #14
    Scott Zuhse is offline Administrator
    Join Date
    Mar 2005
    Posts
    2,627

    Default

    Nice design. A couple of pointers. Be careful with too cold of a circulation as this can promote beer stone bulid up - particularly in vinyl. This is the calcium oxilate that is from the beer. Chill haze.

    Next, with all the work you put into your design, you fell short at the tower. Bridge the vinyl line between your cold blocks and copper with the foil tape and then insulate with your expanding foam.

    What type water pump did you utilize?
    Scott Zuhse, Instructor Micro Matic Dispense Institute

  15. #15
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    What I tried to do was to be sure my system has enough capacity to cool. I think I have achieved that. I am now adjusting the temps upwards on my freezer to determine the best set point to reduce the duty cycle of the freezer. I do not know much about beer stone, thanks for the pointer.

    can you elaborate on the tower modifications? I do not quite understand the method you describe.

    the water pump I am using is a fountain pump from a home improvement store with about 8' of head pressure.

    I was concerned about expanding foam in my tower since it can get between the hose and the copper and then expand and cause separation. should I not worry about that?

  16. #16
    dsuski is offline New Member
    Join Date
    Apr 2009
    Posts
    2

    Default

    Nice job, looks really good. And, yes, I'm curious about the type of pump that you used as well, also could you post a pic of where you mounted it? Didn't see it in any of the pics.

    Thanks!

  17. #17
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    The pump I used was a $38 submersible fountain pump from Menard's. It has an 8' head (max vertical rise). They do no spec it in terms of pressure. If I drain it and then start the pump it takes about 60-80 seconds to pump it the entire 60 feet. 20' each way plus the 20' of copper in the freezer.

    I do not have a picture of it "mounted". It is submersible and has suction cups. If you look closely you can see the two cooling lines. the return line come up and attaches to the copper on the left and in the front. the exit line is behind the copper and goes towards the left into the top of the pump, you can see a black thing there. there is no trick to this, it just sits in the tank.
    Attached Images Attached Images

  18. #18
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    sorry, I got it wrong "the return line come up and attaches to the copper on the left and in the front." I meant to say "the return line comes up and attaches to the copper on the right side and in the front"

  19. #19
    dsuski is offline New Member
    Join Date
    Apr 2009
    Posts
    2

    Default

    Ah, gotcha, now I understand why I didn't see it. I've actually been planning on doing something like this for a while and have been thinking of different ways to do it and the pump's been my biggest curiosity. Thanks for posting this, very cool and helpful. I guess the only thing I'd be concerned about is, (and I only say this from what I've read in some of the forums while researching) that apparently some folks have had some issues with their pumps warming up. Not sure if yours gets warm but just something to maybe check up on. Good luck with it and thanks again for sharing!

  20. #20
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I have not had any issue with the pump getting warm. it was the second smallest fountain pump. I had the smallest one (4' max virticle lift) and it worked, but it had very low pressure and the next size up (8' max virticle lift) was only $3 more. I returned the small one, paid the difference and now I have twice the flow. it is very small, I cannot imagine it generatating much heat. It is about 4"Hx6"Lx3"D, fits in the palm of my hand.

  21. #21
    rhino is offline Junior Member
    Join Date
    Apr 2010
    Posts
    5

    Default

    Any chance of a little more information on the Ranco thermostats?

  22. #22
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I am assuming you mean how to wire them. there are two basic ways to use them. 1. you can simply use them to make an electrical connection (to complete a circuit) and provide a signal to something else (the compressor relay in this case). 2. you can actually use them to power a device( the fans for the fridge). I used them each way.

    this is were I bought it - good price $50
    Ranco ETC-111000 - Ranco - Single Stage ETC Temperature Control w/ Sensor (120/240V Input)

    Here is the wiring diagram from ranco:
    http://www.ntsupply.com/files/produc...tructionsa.pdf

    for my fridge (to power the fans) used figure 4 on page 4.
    for the freezer (the compressor) I used the wires inside the fridge that connect to the temp sensor module and wired them per figure 6 on page 4, making sure I used the 120 volt terminal for both applications, since I am in the U.S. and we have 120 vac power.

  23. #23
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I was looking at another post, he had the link to his pump. this has the same specs as mine and looks identical. I got mine at Menards for $10 less.

    Fountain Pro Pump WT 345 - Serenity Health

  24. #24
    rhdmr2t is offline Junior Member
    Join Date
    May 2010
    Posts
    9

    Default

    so i guess at this point i was wondering a little more about the trunk lines.. you wrapped all lines with the aluminum tape then the other teflon and so fourth.. and the coolant lines have to be a continuous loop correct??? love this post.. just what i was looking for.. was about to pick up a glycol unit and trunk lines but this diy seems to be the trick

  25. #25
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    I simply looked at what was being marketed.

    Yes. As the above pictures show, I modified my T style tower with copper to get all 3 faucets cold. Then you have a cooling line running to your faucets and a return back to the freezer.

    Micromatic also has many good educational pages. They also have some tools for calculating the diameter beer line you need (pressure drop) to get the flow you want and not over or under pressurize your kegs. Kegman has some as well, they have a couple good pages that walk you through the calculations.

    Trunk Line, insulated beer line

  26. #26
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    It seems to be working well. My concern is how long my fridge will last as the duty cycle is probably higher that it was designed for. If you purchase a commercial glycol unit, you will pay $1000 min for the cooler. But you get a warranty and a lot of excess capacity. Right now it seems to be on for about 15-20 mins per hour. As was posted above, I need to insulate my tower better. I may put a fan in the back to move more air past my compressor, that can only help things. I chose a new fridge, since I did not know how much heat loss I would have and newer ones are more efficient, but the heat loss does not seem to be that bad. I started with my freezer at 19F to get 29F coolant, but taking advice above with regard to beer stone, I have bumped up my freezer 4 degrees and things work better, I get about a 1" head on a pint. My keg is at 35F, they say you can get up to 42F. that seems extreme to me, I am only going to move it up 1 or 2 degrees. I do not drink a lot, so I figure the cooler my keg, like anything, it will keep longer.

  27. #27
    Scott Zuhse is offline Administrator
    Join Date
    Mar 2005
    Posts
    2,627

    Default

    Quote Originally Posted by JJtom View Post
    What I tried to do was to be sure my system has enough capacity to cool. I think I have achieved that. I am now adjusting the temps upwards on my freezer to determine the best set point to reduce the duty cycle of the freezer. I do not know much about beer stone, thanks for the pointer.

    can you elaborate on the tower modifications? I do not quite understand the method you describe.

    the water pump I am using is a fountain pump from a home improvement store with about 8' of head pressure.

    I was concerned about expanding foam in my tower since it can get between the hose and the copper and then expand and cause separation. should I not worry about that?
    Your tower design is such that you are requiring the heat transfer from the blocks and copper to maintain the air temperature. This is a design that manufacturers attempted when these systems first became popular and they failed miserably. The upgrade is simple. Using foil tape, join the vinyl line to the cold blocks and copper line. Use short strips but use a significant amount as this will be the heat transfer between the actual circulation versus the vinyl just being exposed to the air temperature.

    Once you have bridged this gap with the foil, the expanding foam will not pull this apart and will act as a vapor barrier to reduce condensate build up. Or use an insulation tape over the foil.

    Beer stone is a major issue in the remote systems at retail stores. The glycol chillers are adjusted down too cold to compensate for a warm keg cooler. This is not what these chillers were designed for. They are designed to maintain the beer temperature between the keg and the faucet. If the beer is too cold (28F or lower) the beer stone breaks away from the beer and tends to coagulate anywhere it can in the system. Particularly on the beer line. Not recommended to circulate your coolant below 29F.
    Scott Zuhse, Instructor Micro Matic Dispense Institute

  28. #28
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    let me see if I understand. You are saying to simply wrap foil tape around my vinyl lines and the copper or cooling block?

    do I need more vinyl tubing or can is just start wrapping, with foil tape, the configuration I have? It does seem to make sense in that the purpose would be to use the foil to conduct the cold directly to the tubing.

    I will work on that. thanks

  29. #29
    Scott Zuhse is offline Administrator
    Join Date
    Mar 2005
    Posts
    2,627

    Default

    Stick the foil tape between the vinyl lines and the cooling blocks / copper lines. Lay it on in multiple layers. Your are building an aluminum block which will transfer heat much more efficiently than the air will. Lay it underneath and over the top of the vinyl. Where there is not any copper, bridge to the blocks. Use the roll if you have to. You have worked hard to design and construct a homemade glycol system but left about four to five inches of line with minimal contact with your heat transfer. In other words, you are making the same mistake manufacturers of these systems made in the 80s.
    Scott Zuhse, Instructor Micro Matic Dispense Institute

  30. #30
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    Got it, makes a lot of sense. Thanks for the extra details.

  31. #31
    JJtom is offline Junior Member
    Join Date
    Jan 2010
    Location
    minnesota
    Posts
    25

    Default

    this has been running several months now and I wanted to provide an update on a couple things I have learned.

    I initially set my freezer with a very narrow cycle band at 3 degrees. This caused it to cycle freqently and caused the thermo protection device to fail. I replaced it for $20, but some places wanted $50. I since changed it to 9 degrees and have my freezer setpoint at 27 degrees. This seems to keep my coolant at around 30 or so.

    The other modificiaiton I made was a add an additonal fan underneath the fridge to curuclate cool air past the compressor. Better safe than sorry was my thought.

    Beer stays cold, first glass comes out fine.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Note:
Micro Matic’s Draft Beer Discussion forum is a public service which allows our members to share their draft beer knowledge and for visitors to view their discussions. While Micro Matic's Dispense Institute instructors and knowledgeable staff are often participates in the forum, Micro Matic does not attempt to verify information posted by members. The information which members post are personal views, and may not reflect the views of Micro Matic. Micro Matic takes no responsibility and assumes no liability for any information posted by members, or results that occur from the information. Micro Matic reserves the right to monitor, remove or edit content at its discretion.