Quote:
Originally Posted by Ritchie View Post
After looking at the replacement part for the BM23, I noticed the the fan that is in my cooler is the wrong one. The guard is missing too. I just repitched the blades so it blows on the coils. It should be moving more air than it is, so I will be ordering a new fan, motor and guard from bev air. Still managed to break the 40°F barrier. got down to 39.5°F. Slowly getting there.
Those units don't move a great deal of air in the first place. It certainly wouldn't hurt to have an OEM fan motor & blade just to be sure.

Have you noticed whether the compressor is cycling on & off or is it running constantly? You might want to order a new temperature control from Bev Air as well. Over the years it may not be as accurate as it used to be. Don't use a control that senses the air temperature. You can run the danger of freezing up the evaporator. Get the one from Bev Air that senses the evaporator temp.

If it is an R12 unit it is at least 14 years old. R12 was phased out in '94.

THE ICEMAN